POWER
IN 3Φ SYSTEMS
Measurement
of three phase power by one wattmeter method
Limitation
of this method is that it cannot be applied on unbalanced load. So under this
condition we have I1 – I2,- I3= I and V1=V2=V3=V.
Diagram is shown below:
Two
switches are given which are marked as 1-3 and 1-2, by closing the switch 1-3
we get reading of wattmeter as P1 = V1I, cos (30-4)= cos(30-6)=√3×VI. Similarly
the reading of wattmeter when switch 1-2 is closed is P2 = V12, cos (30+6) =
√3×VI cos(30+Φ).
Total
power is P1 + P2 = 3 VI cos 0.
Three-Wattmeter Method of Three
Phase Power Measurement
Three
Wattmeter Method is employed to measure power in a 3 phase, 4 wire system.
However, this method can also be employed in a 3 phase, 3 wire delta connected
load, where power consumed by each load is required to be determined
separately.
The
connections for star connected loads for measuring power by three wattmeter
method is shown below.
The
peasure coil of all the three wattmeters namely W1, W2 and W, are connected to
a common terminal known as the neutral point. The product of the phase current
and line voltage represents as phase power and is recorded by individual
wattmeter.
The
total power in a three wattmeter method of power measurement is given by the
algebraic sum of the readings of three wattmeters, i.e.,
Total
Power P = W1 + W2+W3
where
W1
= V1I1
W2
= V2I2
Except
for 3 phase, 4 wire unbalanced load, 3 phase power can be measured by using
only two wattmeter method.
In
the previous lesson, the phase and line currents for balanced delta-connected
load fed from a three-phase supply, along with the expression for total power,
are presented. In this section, the measurement of total power in a three-phase
circuit, both balanced and unbalanced, is discussed. The connection diagram for
two-wattmeter method, along with the relevant phasor diagram for balanced load,
is described.
Keywords:
Power measurement, two-wattmeter method, balanced and unbalanced loads, star-
and delta-connections.
After
going through this lesson, the students will be able to answer the following
questions:
1.
How to connect the two-wattmeter to measure the total power in a three-phase
circuit both balanced and unbalanced?
2.
Also how to find the power factor for the case of the above balanced load, from
the reading of the two-wattmeter, for the two types of connections delta?
Two-Wattmeter Method of Power
Measurement in a Three- Phase Circuit
The
connection diagram for the measurement of power in a three-phase circuit using
two wattmeters, is given in Figure 1.62. This is irrespective of the circuit
connection star or delta. The circuit may be taken as unbalanced one, balanced
type being only a special case. Please note the connection of the two
wattmeters. The current coils of the wattmeters, 1 and 2, are in series with the
two phases, R & B, with the pressure or voltage coils being connected
across R - Y and B - Y respectively. Y is the third phase, in which no current
coil is connected.
If
star-connected circuit is taken as an example, the total instantaneous power
consumed in the circuit is:
Each
of the terms in the above expression is the instantaneous power consumed for
the phases. From the connection diagram, the current in, and the voltage across
the respective (current, and pressure or voltage) coils in the wattmeter, W,
are i So, the instantaneous power measured by the wattmeter, W1 is:
If
this expression is compared with the earlier expression for the total
instantaneous power consumed in the circuit, they are found to be the same. So,
it can be concluded that the sum of the two wattmeter readings is the total
power consumed in the three-phase circuit, assumed here as a star-connected
one. This may also be easily proved for delta- connected circuit. As no other
condition is imposed, the circuit can be taken as unbalanced one, the balanced
type being only a special case, as stated earlier.
Phasor Diagram for a Three-Phase
balanced Star-Connected Circuit
The
phasor diagram using the two-wattmeter method, for a three-phase balanced star
connected circuit is shown in Figure 1.63, the phase currents lags the
respective phase voltages by Φ=Φp, the angle of the load impedance per phase.
The angle, Φ is taken as as the neutral point on the source (N), if it is
assumed to be connected in star. The voltage at that point is zero (0).
The
line voltage line voltage, VRY leads the respective phase voltage, VRN by 30°,
and the phase voltage, VRN leads the phase current, IRN by . So, the phase
difference between V and
Comments
on Two Wattmeter Readings
When
the balanced load is only 1 nly resistive (Φ = 0o), i.e., power
factor (cos Φ = 1.0), the readings of the two wattmeters (W1 =W2
x cos 30° =0.866 (+ve)), are equal and positive.
Before
taking the case of purely reactive (inductive/capacitive) load, let us take
first lagging power factor as (cos p=0.5), i.e., $=+60°. Under this condition,
It
may be noted that the magnitudes of the phase or line voltage and also phase
current are assumed to be constant, which means that the magnitude of the load
impedance (inductive) is constant, but the angle, o varies as stated.
As
the lagging power factor decreases from 1.0 to 0.5, with o increasing from 0°
to +60°, the reading of the first wattmeter, W, decreases from a certain
positive value to zero (0). But the reading of the second wattmeter, W,
increases from a certain positive value to positive maximum, as the lagging
power factor is decreased from 1.0 to 0.866 (= cos 30°), with increasing from
0° to +30°. As the lagging power factor decreases from 0.866 to 0.5, with
increasing from +30° to +60°, the reading of the second wattmeter, W2 decreases
from positive maximum to a certain positive value. It may be noted that, in all
these cases, W2> W1, with both the readings being positive.
If
the lagging power factor is 0.0 ( = +90°), the circuit being purely inductive,
the readings of the two wattmeters (W1 =- W2 x cos (30° +90°) = cos 120° =
-0.5) are equal and opposite, i.e., W, is negative and W2 is positive. The
total power consumed is zero, being the sum of the two wattmeter readings, as
the circuit is purely inductive. This means that, as the lagging power
decreases from 0.5 to 0.0, with o increasing from +60° to +90°, the reading of
the first wattmeter, W, decreases from zero (0) to a certain negative value,
while the reading of the second wattmeter, W, decreases from a certain positive
value to lower positive one. It may be noted that W2>|W|, which means that
the total power consumed, i.e., (W1 + W2) is positive, with only W, being
negative. The variation of two wattmeter readings as stated earlier, with
change in power factor (or phase angle) is now summarized in Table 1.1. The
power factor [pf] (= cos () is taken as lagging, the phase current lagging the
phase voltage by the angle 6) (taken as positive), as shown for balanced
star-connected load in Figure 1.64. The circuit is shown in Figure 1.62. All
these are also also valid for balanced delta-connected load.
It
may be noted that, if the power factor is leading (= negative (-ve)), the
circuit being capacitive, the readings of the two wattmeters change with the
readings interchanging, i.e., W, taking the value of W2, and vice versa. All
the points as stated earlier, remain valid, with the comments as given earlier.
The first one (#1) in Table 1.1 is a special case, neither lagging, nor
leading, with pf = 1.0. But in second one (#2), both readings remain +ve, with
W, <W2. Same is the case in fourth one (#4), where W1 is -ve and W2 is +ve,
with W1| <W2, total power being positive (+ve). For third case (#3), W1 =
0.0 and W2 is +ve, with W2. For last (fifth) case (#5), W1 is - -ve and W2 is
+ve, with W1| = |W2l, total power being zero (0.0).
Power Measurement using One
Wattmeter only for a balanced load
The
circuit diagram for measuring power for a balanced three-phase load is shown in
Figure 1.65.
The
only assumption made is that, either the neutral point on the load or source
side is available. The wattmeter measures the power consumed for one phase
only, and the reading is W=Vp Ip cosΦ.
The
total power is three times the above reading, as the circuit is balanced. So,
the load must be star-connected and of course balanced one, with the load
neutral point being available. The load may also be delta-connected balanced
one, if the neutral pinpoint on the source side is available. Otherwise for
measuring total power for delta-connected balanced load using one wattmeter
only, the connection diagram is given in Figure 1.66. The wattmeter as stated
earlier, measures power for one phase only, with the total power consumed may
be obtained by multiplying it by three.
Example:
Calculate
the readings of the two wattmeters (W, and W2) connected to measure the total
power for a balanced star-connected load shown in Figure 1.67, fed from a
three- phase, 400 V balanced supply with phase sequence as R-Y-B. The load
impedance per phase is (20+j15) Ω Also find the line and phase currents, power
factor, total power, total reactive VA and total VA.
The
power factor of the load is cos 0=cos 36.87° 0.8 lagging, with Φ=+36.87°, as
the load is inductive.
Total
VA =3.Vp Ip =3×231.0×9.24=6.403k VA
This
can be taken as √3.VI =√3×400×9.24=6.403 k VA
Total
power =3. Vp Vp Ip coso =3x231.0×9.24×0.8=5.123k W
Total
reactive VA=3. Vp Ip sino=3×231.0×9.24 sin 36.87° = 3.842k VAR
The
readings of the two wattmeters are:
Example:
Calculate
the readings of the wattmeter (W) connected as shown in Figure 1.68 (a). The
load is the same, as in Figure 1.68 (b) i.e., balanced star-connected one, with
impedance of (20+j5) Ω per phase, fed from a three-phase, 400 V, balanced
supply, with the phase sequence as R-Y-B.
Solution
The
steps are not repeated here, but taken from previous example.
The
phasor diagram is shown in Figure 1.68(b).
The
phase voltage, VRN is taken as reference.
Example
Calculate
the readings of the two wattmeters (W1 & W2)
connected to measure the total power for a balanced delta-connected load shown
in Figure 1.18(a), fed from a three- phase, 200 V balanced supply with phase
sequence as R-Y-B. The load impedance per phase is (14 - j14) Ω.
Also find the line and phase currents, power factor, total power, total
reactive VA and total VA.
The
power factor of the load is cos 0=cos 45° =0.707 leading, with Φ=-45°, as the
load is capacitive.
As
the phase currents are balanced, the magnitude of the line current is√3 times
the magnitude of the phase current, and the value is:
It
has been shown that the line current, IR lags the corresponding phase current,
IRY by 30°.
The
sum of two readings is (3.38 +0.906) = 4.286 kW, which is same as the total
power computed earlier.
Alternatively,
the phase current, Ipy can be taken as reference, with the corresponding phase
voltage, Vry leading the current by the angle of the load impedance, Φ45°. So,
the phase current and voltage are:
The
measurement of power using two wattmeters for load (unbalanced or balanced),
fed from a balanced three-phase supply is discussed. Also presented are the
readings of the two wattmeters for balanced load, along with the determination
of the load power factor from the two readings, and some comments on the way,
the two readings vary with change in power factor of the load, with the
magnitude of the load impedance remaining constant.
The
difference between the star and delta connection are given below in the
tabulated form.